We are among the thousands without power in the northeast. Day four actually, and we've decided to look into generators so that next year's New Year's doesn't involve fears of frozen pipes bursting and hypothermic babies and cats. At the very least we just need enough juice to run the furnace blower, but if we're going to lay down the cash I'd like to know what it would take to get a little more power ... like enough to run a fridge, router, laptop and lightbulb. I know nothing about this sort of thing, but figure there are more than a few experts out there so I call out to the wisdom of the mob. What am I looking for? How difficult is the wiring? What will it cost me? On the extreme edge, what would it take to get off the grid entirely? (And on a side note, thanks to DTE Energy for telling us we had power when we didn't, for losing the ticket for our neighborhood, for telling us it would be back every single day when it wasn't, and for the helpful DTE representative who warned us that our pipes might burst. Thanks.)
This discussion has been archived. No new comments can be posted.

Home Generators (or How DTE Energy Ruined My Holidays)

Comments Filter:
  • tips (Score:4, Informative)

    by fyngyrz ( 762201 ) * on Wednesday December 31, 2008 @02:07PM (#26282445) Homepage Journal

    At a minimum, you need:

    • A fair amount of 14- or 12-gauge wire (wire is expensive... go measure)
      • wire from generator switch breaker to each device
      • wire from generator to generator switch (needs to be underground / outdoors rated)
      • wire from main service to generator switch
      • instructions are generally with generator switch - study hard. Errors can be disastrous
    • A 15A or 20A socket at each power location (fridge, furnace)
    • A manual generator to line switch ($150 or so on Ebay)
    • A generator. I suggest MINIMUM 3500 watts
      Even though a furnace doesn't pull a lot when running, at the time that the blower starts up, there can be a VERY large startup current. The fridge the same, to a lesser extent.
    • A shed -- you can't put a gas generator indoors, generally speaking - very dangerous
    • I strongly suggest a strong table to mount the generator on for maintenance
    • Some way to bolt the table down, and bolt the generator to the table
    • High temperature exhaust hose for the generator (actually kind of difficult to come by)
    • high-temperature pass through for exhaust to go thru shed wall - hot!

    You can get a lot fancier than this, but this will function perfectly as long as you are there to do the switching soon enough after power fails that your building doesn't get too close to pipe-freeze (I wouldn't want to go below 40 degrees f, pipes are often in walls that are cooler than the rest of the house.)

    If that won't do, you're looking at an auto-start system with an auto-generator switchover, and the only thing I can tell you about that is prepare your wallet for deep excavation.

  • Pipes bursting (Score:5, Informative)

    by Shimmer ( 3036 ) on Wednesday December 31, 2008 @02:13PM (#26282529) Journal

    Might be best to turn off the water entirely and drain the pipes rather than risk a burst.

  • by Just Some Guy ( 3352 ) <kirk+slashdot@strauser.com> on Wednesday December 31, 2008 @02:15PM (#26282551) Homepage Journal

    A lot of people in cold climates have backup (or even primary) wood stoves for heat. The main problem is that these have electric fans to blow super-hot air from around the stove's inner box into the room. Now, given that it's cold outside when you're building fires and very hot inside the stove itself, is there some way to directly convert the heat difference into enough electricity to drive the stove's fan?

    Seriously, these things can potentially put out tremendous amounts of heat, probably enough to keep the pipes from freezing in a medium-sized house and certainly enough to cook simple foods. I'd think that a self-powered version would be extremely appreciated.

  • by Muad'Dave ( 255648 ) on Wednesday December 31, 2008 @02:15PM (#26282555) Homepage
    I just built a new house, and had a 20kW Generac air-cooled generator [generac.com] installed along with a 200A automatic transfer switch and buried 1,000 gallon propane tank. It can run on propane or natural gas, and is manly enough to run my whole house. I have heat pumps with backup propane furnaces. The outside units are small enough so that I do not have to sequence the startup of the compressors, but I could do that if necessary (and may anyway). It self-tests once a week. All told, minus the tank (since many/most of you will have NG service), about $8,000 installed and tested. Well worth it for totally automatic, no-worries switchover even if we're away.
  • by Wonko the Sane ( 25252 ) * on Wednesday December 31, 2008 @02:16PM (#26282557) Journal

    Bottom line: Permanent home backup generators can be purchased for $3000 - $6000 + installation labor.

    If you have natural gas available then I highly recommend using it for your backup generator, since outages are very rare and you won't ever need to worry about storing fuel.

    If you house is like most, then your incoming service is 100 amp/220 split-phase. This means that a ~22 KW generator would give you 100% backup, but really most people don't use more than 80% of their service, so this setup [mainpowerconnect.com] should provide full capacity backup for almost anyone. If that's not enough, then move up to the 30 KW model. Kohler makes generators big enough to power your entire neighborhood if you are willing to buy it.

    Wiring is not difficult, but depending on your experience level and your desire to obey the local electrical code, you should consider hiring a licensed electrician.

  • The dirty way (Score:5, Informative)

    by ShooterNeo ( 555040 ) on Wednesday December 31, 2008 @02:20PM (#26282613)

    There's a dirty, and illegal way to do it.

    First, if you follow these instructions, remember this KEY STEP
                      TURN OFF THE MAIN SWITCH. Also, NEVER turn that main switch on if the generator is running.
                      Finally, the main switch MUST be double throw.

    Forget to follow these instructions, and you can very easily kill a lineman or blow up your generator.

    Anyways, you just need a three pronged dryer plug, 2 of them, and sufficient length of heavy gauge wire. You create an illegal male - male 3 pronged plug, and connect your generator socket into the 3 pronged plug in your house used for the clothes dryer.

    The reason it is illegal is because this form of installation does not prevent you from connecting your generator to the wiring outside your house. If you left the main switch on, you can energize the dead lines outside with 12,000 volts and kill a lineman.

    The advantage? As long as the main switch is double throw, and you don't turn it on when the generator is connected, it is pretty safe. And cheap : a double throw switch and circuit box is $200-$500, while this method can be done for $10.

  • Re:Pipes bursting (Score:2, Informative)

    by Nuitari The Wiz ( 1123889 ) on Wednesday December 31, 2008 @02:21PM (#26282619)

    Actually this is much worse as your risk having the pipes connecting the house to the aqueduc burst.

    The best way is to have a small thread of water running from a faucet, for both the hot and cold water taps. Depending on the layout of the plumbing there might be a need for 2 or 3 faucets to be running.

  • My recommendations (Score:5, Informative)

    by rongage ( 237813 ) on Wednesday December 31, 2008 @02:21PM (#26282621)

    The first thing you want is a natural gas powered generator, not gasoline. Nothing like having to take a trip to the local gas station (presuming THEY have power) to fill up the generator every 8 hours or so. This, by definition, will make the generator a stationary unit (not on wheels, designed to be bolted down to a concrete pad).

    Next, you want a generator with auto-start, auto-transfer with manual return. You want the thing to automatically kick in if the power dies, but YOU should be in control of when it decides to return to the grid. Nothing like finding out that the power died 10 minutes after you and the family left the house for a couple of days and coming back to a cold house with no power and potentially burst pipes.

    Wattage - you will want at least a 5000 watt unit for whole-house use. Forget this idea of running power cords everywhere - unless you like the idea of tripping over power cords everywhere. With the transfer switch mentioned above, the generator takes the place of the grid so your internal house wiring will continue to serve it's duty.

    There are several manufacturers of house generator systems. You can find low-end units at places like Home Depot or Lowes. Better units are best obtained from an electrical wholesale house.

    Do yourself a huge favor here and hire a licensed electrician to do the work. It'll get done right the first time, the electrical inspector won't get excited (in a negative way) when he sees the work, and the odds of "something going wrong" go way down.

    From another guy in Michigan (Westland)...

  • by zarthrag ( 650912 ) on Wednesday December 31, 2008 @02:21PM (#26282629)
    In addition, these types of generators (in the 10kw and under range) can even run on propane in the super rare event of a gas outage - ours accepts dual propane tanks and can run 12 hrs - not that we've ever needed to resort to that.
  • by corsec67 ( 627446 ) on Wednesday December 31, 2008 @02:22PM (#26282649) Homepage Journal

    A lot of people in cold climates have backup (or even primary) wood stoves for heat.

    In Colorado, the only kind of wood stoves that I have seen that use electricity are pellet stoves [wikipedia.org], whereas wood stoves don't need any power at all. You just put logs in, get them burning, and that is it. Are you talking about a wood burning whole house furnace with forced air? That isn't exactly a "wood stove".

    My family primarily uses wood to heat the house, with trees we cut down from the neighbors property. The forest here is significantly overpopulated, so a lot of the trees need cutting down anyways.

  • Re:tips (Score:5, Informative)

    by Anonymous Coward on Wednesday December 31, 2008 @02:22PM (#26282657)

    No way man - you don't need anything nearly that complicated. Since you're just covering an occasional power outage, you don't need anything permanent. Just put the generator outdoors, and run a long extension cord (or a few) inside.

    Make sure the generator is in a locked location, or at least chained down. They have a tendency to sprout legs during emergencies.

    If you want something permanently in place, you need an electrician, and no less. Because you need a huge On-Off-On lever switch to ensure you never attempt to power the house from both the generator and grid simultaneously.

  • Re:tips (Score:5, Informative)

    by MightyMartian ( 840721 ) on Wednesday December 31, 2008 @02:24PM (#26282677) Journal

    I just ran heavy (15amp rated) extension cords this year when our power went out. I'm wiring up my shed this spring, so I'll already have a back ho out digging the ditch to run the underground wire, so I'm going to run a spare three pole 10-gauge direct burial (will cost some bucks) along with the main run out to the shed. I'll wire up a few outlets around my house that connect specifically to the generator (which is an el-cheapo Walmart 3500 watt gas unit), because a) the generator ain't big enough to power my panel and b) to do so in my neck of the woods requires a cut off so you're not rendering your incoming power line hot.

    A bit of advice I got when I bought the generator was that you don't need to run your fridge and freezer all the time, providing you open them infrequently. Every few hours just plug them in, let the compressors bring the temperature down, and then unplug them. At the very least, don't keep the fridge door open while you ponder whether to use hot mustard or not. As you say, many electrical devices that don't draw a lot of power while in use can draw a lot of power at startup (cranking is I think the technical name). Even TVs can draw considerable juice when you first turn them on, so you probably will not want to put all your devices and appliances on a power bar and then flip the switch, but rather turn on each device one at a time.

    Another thing my manual makes very clear is that the generator should be properly grounded. I didn't do that this year, but as I said, when I wire up my shed, I'm going to have to use a grounding rod anyways (since I'm putting in a subpanel) so I'll just bond the generator to that. 20 amps and 120 volts is enough to cook you good in the right circumstances.

  • by Cyclopedian ( 163375 ) on Wednesday December 31, 2008 @02:24PM (#26282681) Journal

    If you get the chance to move out, consider getting a Passive House, where it has super-thick insulation and is hermetically sealed. You wouldn't have to worry about frozen pipes in that kind of setup.

    http://www.nytimes.com/2008/12/27/world/europe/27house.html [nytimes.com]

  • Re:tips (Score:5, Informative)

    by Muad'Dave ( 255648 ) on Wednesday December 31, 2008 @02:24PM (#26282685) Homepage
    I wouldn't go the route of running all that extra wire. They sell 6 circuit generator switches [homedepot.com] for that exact purpose - you move the desired circuits from your main panel into this little box, and hook you generator to it via a standard twistlock connector on a flexible cord. When the power fails, roll the genny to the panel, plug it in, fire it up, and flip the switch. If you know evil weather is coming, pre-stage the genny and cover it with a barbecue grill cover until you have to fire it up. Once it's hot, rain and snow won't bother it.
  • Re:tips (Score:5, Informative)

    by InlawBiker ( 1124825 ) on Wednesday December 31, 2008 @02:28PM (#26282737)

    I've gone through enough power outages to do what you're wanting. This is a good list but I can simplify it a bit.

    1. You'll need a transfer switch to connect your generator into your home's wiring. It is possible (but probably illegal) to back-feed your generator into your home. Improper backfeeding will send power back up the line, creating a danger to the line workers.

    A transfer switch essentially allows your generator to become the power source to your home while cutting off your city power. You can do this yourself or hire an electrician, it's not real expensive. Here's a simple diagram [electrical-online.com].

    2. Next figure out what size generator to get. There are many calculators out there to guide you. Essentially you add up the wattage of each appliance and buy a generator with about 20% extra.

    An example, I have a 3000w generator, it runs 2 fridges, the gas furnace fan, most of the lights, maybe some music. It's very quiet and luggable. We turn off lights when not in use and leave the TV off, but could probably run it.

    Depending on how close your neighbors are you might want to check the decibel level of your gen-set. The cheapo ones work great but are very loud.

  • Comment removed (Score:2, Informative)

    by account_deleted ( 4530225 ) * on Wednesday December 31, 2008 @02:28PM (#26282743)
    Comment removed based on user account deletion
  • by hAckz0r ( 989977 ) on Wednesday December 31, 2008 @02:32PM (#26282795)
    When you wire in your core devices that need continued power it is good to use a set of automatic transfer switches. When the grid power is up the electricity flows like normal, but when the generator us up the switches divert the inputs for those devices to the generator. When your power comes back up you simply turn off the generator and everything goes back to normal. If you buy the expensive whole house generator models they should come with this equipment, but you can buy them at your local hardware store, or eBay, for the low end generators. Having everything pre-wired saves a lot of fumbling around in the dark playing with kinked cords and potential high voltage, and a lot fewer headaches. No more pulling all refrigerators out just to plug them into the generator any more. Been there, done that. What I have that needs power has it as soon as I turn the key and pull the cord.
  • by tgd ( 2822 ) on Wednesday December 31, 2008 @02:32PM (#26282801)

    Every state and town has different rules about how it all needs to be set up.

    In some places, like Massachusetts, you can't do any of the install yourself. You have to have a licensed electrician do it.

    As a tip, get a generator that uses an inverter. They run quieter and are less likely to damage electronics if you run out of fuel with them.

    You also, pretty much everywhere, have to have a proper transfer switch to disconnect the grid power any time there is any electricity being sent into your house by the generator -- otherwise you will energize the power lines around your house and could kill a line worker.

    But generally, you really need to talk to someone who knows the answer locally for you.

  • by mykepredko ( 40154 ) on Wednesday December 31, 2008 @02:33PM (#26282819) Homepage

    Just a comment - we've had a Kohler 15kW Natural Gas powered generator that automatically comes on if power is interrupted for more than 10 seconds for the past year. We've needed it a couple of times now for multi-hour interruptions and it's worked well with the following comments:
    1. Get an electrician that knows what he's doing and has experience with automated generators. I spelled out how everything was supposed to be wired and the bozo our contractor hired didn't trust my work beforehand and refused to wire up things like our refrigerator because he thought it drew too much current and then didn't believe my calculations
    2. When you look at different generators, you will see that going to a water cooled unit (which is generally what you get when you are in the 22kW range) doubles the price. The 15kW units don't power the whole house, but more than enough to be liveable - you should get your Furnace, Air Conditioning (power goes out in the summer too), kitchen, basic computers & internet service, a couple of bedrooms and a TV/etc. working comfortably
    3. The generators need maintenance. Plan on $500 or more a year - you can't do this yourself unless you are licensed for working around natural gas.
    4. The units will test themselves once a week. Make sure they come on when nobody's going to be bothered
    5. Don't try to do it yourself, the installation is somewhat expensive ($1,500-$2,000) and then you have to do the interior wiring (hooking up the Automated Transfer Switch (ATS) and deciding which circuits should be used).
    6. The pricing of the units change during the year and what's going on. Right now would probably be the worst possible time to buy one - I wouldn't be surprised that their prices haven't doubled in your area. You should be looking in the late spring before hurricane season is the best.

    myke

  • by TheMeuge ( 645043 ) on Wednesday December 31, 2008 @02:34PM (#26282839)

    They are very reliable, and like you mentioned they are SIGNIFICANTLY quieter than the competition. If you have to have it rumbling overnight, the difference may be enough to warrant spending more. Also, be careful with power ratings, as they can be PEAK or MEAN. A 1kw honda could probably push >0.8kw all night. A 3.5kw (peak) no-name brand may not actually be able to do that.

    I recommend Honda because a number of people I know have recommended them highly. Ultimately, that's my major source of information, as I do not own one myself.

  • Re:tips (Score:4, Informative)

    by hardie ( 716254 ) on Wednesday December 31, 2008 @02:37PM (#26282861)

    "I know nothing about this sort of thing.."
    I strongly advise having someone who does do the installation.
    You *must* have a switch that disconnects your house from your service drop. This is not a small switch--typical would be a 100A disconnect. If you don't, your generator will feed the service and present a huge danger to the people trying to restore your power. Ours allows the house to be powered off of either the generator or the utility, with no way for the utility and generator to be connected.

    We bought an 8kW generator when we moved to Maine five years ago. My first thought was to buy a larger unit, but there's a problem with this idea. Compare fuel consumption fully loaded and at half load. IIRC, half load still consumes about 3/4 of the full load fuel. Generators become much less efficient at low loads--this means that you want to size it right, not oversize it. Running a generator isn't cheap.

    I added up what we would typically have running and I think I came up with 4 or 5 kW. Bumping it up to 8kW seemed reasonable. Everything runs fine except the microwave (which acts browned out), and I don't use my plasma cutter or arc welder when we're on generator.

    Steve

  • some ideas (Score:5, Informative)

    by scharkalvin ( 72228 ) on Wednesday December 31, 2008 @02:41PM (#26282921) Homepage

    Generac (http://www.generac.com/Default.aspx) sells complete packages ready to install as well as discrete units and transfer switches. I have one of their 15KW air cooled LNG/Propane generators (only in my case it is for power outages caused by Hurricanes). Very easy to install, mount their transfer panel next to your main breaker panel and transfer some of the loads from the main panel to the generator panel. The unit WON'T run your entire house, but you can put the most important circuits under backup.

    If you have piped in LNG this is the way to go. Otherwise you need to bury a 250 to 1000 gal propane tank in the backyard.

        The choice of fuel for generator use would be LNG, Propane, Diesel, and Gasoline (in that order).

    Gasoline has the shortest 'shelf life' and is the most difficult to store (ask your fire department!).

        Diesel fuel can last for years with the right additives and can power your car (if you have a diesel car). Diesel engines will also run on JetA (live near an airport?), home heating oil (filter it first!), bio-diesel (rob your nearby McDonalds of their used french fri oil!), even Kerosene. If you buy diesel fuel for generator use make sure you fill out the required paperwork so you don't have to pay the road taxes on the fuel. You can store diesel in the same kind of tanks that home heating oil is stored in.

  • by Glendale2x ( 210533 ) <slashdot@ninjam o n k ey.us> on Wednesday December 31, 2008 @02:45PM (#26283001) Homepage

    There's two ways: the "emergency only" way and the fancy everything automatic way.

    #1: Any gas generator with a 240/120v twist lock outlet plus one of those 6 to 10 circuit generator transfer switches. The transfer switch has rocker switches on it and you pick your favorite circuits that you want to run on the generator during an outage. It wires in next to your breaker box - no need to run new wire anywhere. They usually have watt meters on them, too. When the power goes out, plug the generator into the transfer switch, fire it up, and switch the circuits to emergency. Get a generator in the 5 to 10 kW range. Cheap and effective, but the downside is you have to start it manually, and most portable units you can find run on unleaded gas. Make sure you run the generator at least once a month or you'll be in a world of hurt when you need it the most and it doesn't want to start.

    #2: The fancy automated way. Get one of those Generac whole-house units. They have automatic transfer switches that completely bypass the utility feed and run the whole panel. When the power goes out it auto-starts and auto-transfers. They automatically start to exercise every week, too. These will probably be special order and definitely more expensive, but well worth it if you frequently have extended power outages with crappy weather and you don't want to go outside to fire up the generator. They can run on natural gas or propane. Get at leat a 10kW unit.

    Either way you go use a transfer switch that wires into your breaker panel. It's much easier than running new wire or extension cords everywhere, especially when the power is out and you just want to get the damn thing running.

  • by Wonko the Sane ( 25252 ) * on Wednesday December 31, 2008 @02:48PM (#26283039) Journal

    The 15kW units don't power the whole house, but more than enough to be liveable - you should get your Furnace, Air Conditioning (power goes out in the summer too), kitchen, basic computers & internet service, a couple of bedrooms and a TV/etc. working comfortably

    That would depend on exactly how your house is configured. Heating, water heater, clothes dryer and stove could be gas or electric. If all of those were gas, then 15 KW should be more than enough for all your other loads.

    If you take your electric bill and divide kilowatt-hours by the number of hours in the billing cycle then you would get your average consumption. That would be a good starting point when you decide on a generator rating.

  • Re:tips (Score:3, Informative)

    by gavinsgramma ( 1442317 ) on Wednesday December 31, 2008 @02:49PM (#26283061)
    We purchased a Natural Gas powered from a store here called Farm and Fleet. It has it's own breaker box and it automatically switches over to generator with in short period of time after the power goes, there is some delay since our power sometimes just flickers. It also kicks off when the power returns. It powers all of our refrigerators, freezers sump pumps, furnace pump, some lights and of course the computer equipment. You can get them to power the entire house. Ours was about $1700. for the generator and another $1000. to install. It works well. You can also get them to run off of LP gas if you do not have access to natural gas. When they installed they ran wire from the main box to the generator box so you do not have to run wire that far.
  • Disclaimer: Electricity is dangerous, and can kill you. I am not an electrician. I am a slashdot poster.

    The short answer for going-off grid: Buy lots of solar panels, which don't work as well here in SE Michigan (WTF is with you calling Michigan the "Northeast"?) in the winter time, but may be enough to get you by in conjunction with a good sized battery bank, and be prepared to significantly change the way you use electricity.

    As for the short / halfass way most of us deal with generator usage: Backfeeding (which isn't always regarded as the safest / smartest thing to do, since there are always idiots out there that will screw it up)

    -Go to your breaker box, shut off the main breaker or breakers (the ones at the top of your box that say "Main".)

    Congratulations, your house is now just a giant circuit of wires, not connected to the grid.

    -Shutoff any and all non-essential breakers, especially those connected to heavy draws (You're not going to run your electric stove unless you've got a beefy generator). You may just want to kill everything, then try individual breakers on over time.

    -Fire up your generator. If your 401k is where mine is now, you may want to do this indoors, in a confined space....If breathing is a priority for you (pussy), do this outside, a reasonable distance from your house.

    -Using a heavy gauge extension cord (Not a "move a lamp" cord, think "run a heavy appliance / machine" cord), plug in to a nearby outlet.

    Congratulations, you are now "backfeeding" your house off the generator. Instead of coming from the power lines, your electricity is coming in through an outlet. *DO NOT TURN YOUR MAIN BREAKERS ON!!!* One, Your poor generator will now try to power the entire grid, something that no dinky little 2500watt Honda can do and two, you will send power down a line that the poor DTE linesmen will / may assume is dead. Improper backfeeds can kill (and usually do a few times a year).

    Now you try and figure out what "side" of your box is being feed (if you have a typical, grey box with switch type fuses in two columns. If you have glass fuses in a quaint old house....call an electrician and move out. Oi). The breakers on the same side as the circuit your generator is plugged in to will now have power. If it's on the same side as your furnace, you can turn the furnace breaker on and, hopefully, the furnace should kick on and begin heating the house. If your furnace is on the other side as your power source, you can move the power line to an outlet that is on the same side, or plug in another extension cord from your generator to an outlet on the same side.

    Once power returns to your area simply shut down your generator, unplug your cords, then turn your main breaker back on.

    You have to prioritize what's important to you for power. Furnace and sump pump are your musts, and a sump pump can put out a very heavy load for a very short time, causing a brownout. Ditto a Refrigerator. After that, its your call based on what the generator will power. You can try to power your whole house on a 2000 watt generator, and the generator will run. You'll also kill the generator and probably damage your major appliances. Bigger the generator, the more you can power, and the greater the cost. Honda is the Sony of the Generator market. Generally quality stuff, but you'll pay for it.

    You'd also do well to investigate your electrical box and spend a day labeling every breaker and determining what you have running on each circuit. (lest you find out that a cheap alarm clock shorted out while you were on vacation, causing a breaker to pop, and that breaker was the same circuit your sump pump is on, which explains why your basement is now a swimming pool.) When I moved it, my box had two labels "Furnace" and "stove", now all 22 circuits are labeled, and I've been putting together a diagram that covers every outlet in the house.

  • by u38cg ( 607297 ) <calum@callingthetune.co.uk> on Wednesday December 31, 2008 @02:52PM (#26283107) Homepage
    Make sure your mains switch is double throw; some just open the live side. If this is the case, the guy who is trying to patch your power lines back together will die when you fire up your generator. Power companies get snarky about householders killing their staff.
  • by Just Some Guy ( 3352 ) <kirk+slashdot@strauser.com> on Wednesday December 31, 2008 @03:02PM (#26283251) Homepage Journal

    Not quite. This style of wood stove (common in the Midwest at least) has fans built into its structure. The fire box sits inside a larger metal box, and the fans force air between the two. This lets you burn a fire much hotter than you normally wood and uses ambient room air to keep the whole system safely cooled. If the internal fans aren't blowing, then the fire box is effectively wrapped in a blanket of unmoving air. The insides would overheat while the outside would radiate a lot less heat than, say, a Franklin stove.

  • Safety comments (Score:3, Informative)

    by tomdarch ( 225937 ) on Wednesday December 31, 2008 @03:04PM (#26283293)
    Sorry to be Captain Safety, but I just want to point out the obvious: 1. Be very careful when using a generator - they produce lots of carbon monoxide and kill several people a year. Don't run them in an attached garage - even with the door open. 2. Only a qualified electrician should make the kind of wiring changes that are required to add a generator to a house electrical system. The building code requirements are complex, but more importantly, the potential for a fire that would burn down your house is very real. Personally, I'd rather go without electricity for a few days than either die from carbon monoxide poisoning or have my house burn down. Enough with the doom and gloom - adding a generator to a house electrical system is done frequently and generally isn't exceptionally complicated. It's worth it to hire an experienced, licensed, insured electrical contractor to do it right.
  • Re:The dirty way (Score:5, Informative)

    by vlm ( 69642 ) on Wednesday December 31, 2008 @03:07PM (#26283341)

    Forget to follow these instructions, and you can very easily kill a lineman or blow up your generator.

    1) Far more likely you'll vaporize your generator. Hook up a 3 KW generator to an entire neighborhood drawing maybe 300 kW and your generator goes poof. The only way you'll kill a lineman if the broken line feeds only your house and the break is an open circuit as opposed to short. Worst case is in between, turning a torn line tangled in a tree into a multi-KW space heater... Kind of like one of those electric charcoal starters but on a much larger scale.

    2) The "real" reason it's illegal is, as you'll quickly discover, a male to male cable will probably fall out of the dryer plug at some point and then you've got a couple KW at 220 volts on large bare copper connectors less than an inch apart in a pitch dark room on the floor, or perhaps it'll hit something somewhat conductive on its way to the ground and start a huge fire, or perhaps the kids will play with it and get vaporized. The most likely failure mode of this experiment is electrocution of yourself and/or your family rather than a lineman. After all, the linemen are already working with live power on the "other" side of the broken line... they know what to do, and you don't.

    3) You'll also quickly discover that you can't start up your furnace, water heater, sump pump, TV, and microwave all at the same instant although they may all run steady state. Expect alot of fun when the fridge and sump pump simultaneously start up, especially at 2am. You'll get lots of practice reseting breakers and restarting the generator.

    4) Built in "permanent" generators are generally built to run and refuel 24x7. "Portables" generally are built to run a tankful and get put away till tomorrow. Portables will have some inherent design engineering "issues" such as gas caps next to red hot mufflers. So be really careful whem refilling. Hurry up and you'll turn into a torch. Also your 4 cycle will inevitably run out of oil at some point, hope you're checking the oil and/or the low oil shutoff works before the engine is trashed.

    5) Since this is probably one of the most dangerous things you can possibly do, try not to do anything without thinking about each step very pessimistically. Also no booze, no waking up at 2am to refuel while half asleep. The greatest danger is doing something stupid, and being lucky, so you do it again until you croak.

    Other than that, no problem.

  • by Captain Nitpick ( 16515 ) on Wednesday December 31, 2008 @03:29PM (#26283689)

    Nothing like having to take a trip to the local gas station (presuming THEY have power) to fill up the generator every 8 hours or so.

    THIS IS A MAJOR ISSUE.

    When you have a massive area-wide power outage, three things happen with regards to gas stations.

    First, many of them lose power. Gas pumps do not run without power. Until the station itself gets generators set up, it's useless.

    Second, everybody else with generators is going to be crowding into the gas stations to try to buy fuel.

    Third, odds are whatever caused the widespread power outage is also screwing up the fuel distribution system. The gas stations may not have any fuel to sell.

  • Re:tips (Score:2, Informative)

    by resonance ( 106398 ) on Wednesday December 31, 2008 @03:34PM (#26283775) Homepage

    As you say, many electrical devices that don't draw a lot of power while in use can draw a lot of power at startup (cranking is I think the technical name)

    I've seen it called "Inrush Current"

  • $100 1KW Generator (Score:3, Informative)

    by oldzoot ( 60984 ) <morton.james@co m c a st.net> on Wednesday December 31, 2008 @03:48PM (#26283963)

    John DeArmond has a good article on his site about the $100 1KW Chinese-made generators sold at Northern Tool.

    http://www.johndearmond.com/2008/12/24/the-generator-that-could/ [johndearmond.com]

    Enjoy,

      OZ

  • Re:tips (Score:3, Informative)

    by Muad'Dave ( 255648 ) on Wednesday December 31, 2008 @03:55PM (#26284071) Homepage

    ...I'm going to run a spare three pole 10-gauge direct burial (will cost some bucks) along with the main run out to the shed.

    You might want to check to see if #6 aluminum wire is cheaper than #10 copper. Since you're going to run it between panels, it should be no problem - they all seem to have Cu/Al lugs and a little NoAlOx goes a long way. That'll give you some spare capacity, too. (#10 copper UF = 30A, #6 Al UF = 40A).

  • Bury the noise (Score:3, Informative)

    by SgtChaireBourne ( 457691 ) on Wednesday December 31, 2008 @04:15PM (#26284317) Homepage

    ... The things get pretty darned LOUD tho....but, I've heard that the Honda ones...at a premium price, and very, very quiet....

    If you put the generator in a hole in the yard, you'll have a night-and-day difference in noise levels. Just make sure that it is well-drained and set up so that no one will fall into it. Under the deck or patio is often good.

  • Re:The dirty way (Score:3, Informative)

    by xrayspx ( 13127 ) on Wednesday December 31, 2008 @04:19PM (#26284359) Homepage
    A less scary way is to run whatever you want to run through a relatively large APC, and plug the APC into the generator. I found a 3000w APC was enough to power 15 machines long enough for me to get my homemade romex extension cable and get the generator running.
  • Re:Pipes bursting (Score:3, Informative)

    by Admiral_Grinder ( 830562 ) on Wednesday December 31, 2008 @04:47PM (#26284719)
    The drain pipes in the yard may not freeze, but what about all your sink drains? You would have to add RV anti-freeze to them and then you wouldn't be able to use them (have to keep adding more back to them). You don't want to drain your traps...you wouldn't like the smell very much.
  • by Anonymous Coward on Wednesday December 31, 2008 @05:12PM (#26284979)

    CAUTION: YOU MAY KILL SOMEONE IF YOU DO NOT TURN YOUR HOUSE'S MAIN BREAKERS TO OFF!
    * If you leave the Main Breakers ON you will backfeed power to the entire neighborhood, and the power workers think the lines are dead. Very bad.
    * Technically, you need an electrician to wire a breaker/cut-off switch to the generator. In this manner when you switch the generator connection to ON you also switch the Main Breakers to OFF. Expensive, but safe and complies with NEC.
    * Most people just use a male to male plug, plug one end into the generator, and the other into some house outlet. If you turn the Main Breakers OFF ~BEFORE~ you do this, it is possible to get power to everything in your house, limited by the breaker capacity and the power generation capacity, and not feed the neighborhood. The relative safety of this is up to others to argue.
    * IF THIS MAKES NO SENSE TO YOU, SEEK PROFESSIONAL HELP. Or at least a neighbor with a subscription to Popular Electronics. Your local linemen will thank you!

  • Re:tips (Score:2, Informative)

    by schwinn8 ( 982110 ) on Wednesday December 31, 2008 @05:23PM (#26285117)

    It should be noted that many generators don't always put out a true sinusoidal wave, and some also don't put out the proper "120VAC" - they drift up or down depending on load, capacity, and changes in the load. For this reason, many logic-level electronics may have issues with generator power. Motors tend to not care as much (though they can make funny noises on the weird waveform) but more sensitive electronics can simply fail due to the voltage or waveform issues. A friend of mine in NH recently blew his furnace's logic-boards (oil furnace) while on the generator. He was told that his logic boards were more sensitive than the replacements, but the furnace-guy told him this was common on generators.

    All I'm saying is, beware of running fancy electronics on generators, unless you get a line conditioner that can modify (buck/boost) the voltage and clean up the sine wave.

  • Re:tips (Score:5, Informative)

    by Harik ( 4023 ) <Harik@chaos.ao.net> on Wednesday December 31, 2008 @05:41PM (#26285321)

    Indeed. A 200 amp manual transfer switch can be found for $400 online. This gives you the ability to have a male plug coming out of the transfer switch that can never be powered by the utility - if it's connected, the mains are disconnected.

    They usually come in the form of a breaker box. Installation isn't trivial, but it's not exceptionally difficult. First, identify what circuits are "must have" during a blackout. This would be:

    • furnace blower, HVAC (in hot climates like florida)
    • food storage (fridge, freezer, deep freeze)
    • lighting
    • well pump if you don't have city water,
    • pipe heaters for those of you up north
    • food prep - electric ranges are probably too much load, but you may be able to run a small or midsize microwave. If you have a gas stove with electric controls, power it as well.
    • a few marked outlets specifically as on generator, so you can charge phones/run your laptop/listen to the radio/whatever.

    Next, wire in your transfer switch to your main breaker box. Some go on their own 200amp breaker, others may be wired directly to the rails. TURN OFF YOUR MAIN BREAKER BEFORE WORKING ON YOUR SYSTEM. Read the manual to your transfer switch carefully, incorrect installation can be extremely dangerous.

    Once the new subpanel is installed, you can move your protected circuits to it one-by-one. With mains power off, remove the breaker from your main panel, put it in the subpanel, and move the associated wires. Don't forget to replace the hole in your main panel with a blank, or you'll have a safety hazard. Once all the circuits are transferred, make a male plug for the AC input to the transfer switch that uses a heavy gauge connector (200a for a 200a switch). You may be able to skimp there as long as your extension cord is rated above the BREAKER on your generator. Not the rated power, but what it actually trips at.

    With all that, a startup tip would be to power up the generator, turn OFF all the circuits in the subpanel, switch the input to the generator, and power them up one by one.

    And please PLEASE check local code before trying this yourself. I have left things out that vary from state to state, and some other details that you have to know before trying something like this (what gauge wire to use between the main panel and your transfer switch, for instance). If you have a friend who is a LICENSED electrician you should definitely ask them to look over your plan, and inspect your final work before you use it.

    Finally, not every locale allows owner-improvements to electrical systems, and you may have to use a licensed contractor.

  • Re:tips (Score:3, Informative)

    by mmontour ( 2208 ) <mail@mmontour.net> on Wednesday December 31, 2008 @05:54PM (#26285465)

    I have always wondered are there generators that can run off (for those that have it) natural gas or propane?

    Yes, and you can even get ones designed to provide heat / hot water as well. Link [marathonengine.com].

  • by rewt66 ( 738525 ) on Wednesday December 31, 2008 @06:00PM (#26285515)

    After you turn off the main breaker, put a padlock on it. This prevents anyone who "wants to be helpful" or "knows what they're doing" from turning your main breaker back on.

    Also note that your house probably has two phases. With this approach, you probably need to wire them together. If you do this in the house breaker box, do it before you connect your alternate power. Note well: Anything that depends on 220 V power is unusable with this approach. That may well include the high settings on an electric range.

    We did this for three days in a winter storm when I was a kid (neighbors were on the corner and had power up a different street; they ran us an extension cord). These tips I learned from watching what my dad did.

  • Re:Bury the noise (Score:4, Informative)

    by JWSmythe ( 446288 ) * <jwsmythe@nospam.jwsmythe.com> on Wednesday December 31, 2008 @06:03PM (#26285549) Homepage Journal

    Rather than digging down, you can build up a small hill for the same effect.

        I bought two generators in the last few years. One was a Coleman 5500 watt, and one was a generic Chinese made 5500 watt from Walmart.

        I put the Coleman in my RV, as a temporary power source for air conditioning for a drive. Bad idea. It was so loud, even though the RV is 40' long, I couldn't talk over the sound of it. Driving, it sounded like a Harley was parked beside me. That lasted for about .. umm .. 5 miles. :)

        The Chinese one had what looks like a small car muffler on it. It's only about half as loud.

        Besides the noise level is the reliability of the generators. Both sat for the same period, about a year. Neither one would start. The Chinese generator's spark plug was oil fouled. I cleaned it, and it started right up. The Coleman has some mystery carburetor problem. It still won't start. I suspect even after cleaning the carb, I must have not gotten all the passages cleared.

        But, back to your idea... A hole will get full of water, bugs, or whatever. It may get filled by small children falling into it accidentally. A built up hole would be a better choice. Pick your spot, put down a firm foundation for the generator (a few bricks in the ground would do), put together sides around it with say lattice and screen. A few feet of 2" PVC at the bottom would be a good idea to get rid of any rain water that soaks in. Backfill dirt around it to make a small hill. A piece of plywood (preferably secured somehow) would be a good idea to keep things from falling in when you don't want them to (again, kids, water, stray animals, etc). It would be a good idea to be able to secure it open, yet covered. so if it's raining or snowing (depending on your environment), that won't get all over your nice generator that you've protected so well.

        It'll also make for a nice bunker when the revolution comes to your neighborhood. :) Just watch out for incendiary rounds near the fuel tank. Well, for that matter, near yourself too. :)

  • Re:tips (Score:1, Informative)

    by Anonymous Coward on Wednesday December 31, 2008 @06:15PM (#26285687)

    No, NOT BX!!

    UF wire. "UF" = Underground Feeder.

    Yes, you can direct-bury UF, but the depth depends on many factors, so look it up.

  • Re:tips (Score:5, Informative)

    by xous ( 1009057 ) on Wednesday December 31, 2008 @06:20PM (#26285745) Homepage
    This shouldn't even be suggested. Buy a bloody ATS. http://en.wikipedia.org/wiki/Transfer_switch [wikipedia.org]
  • It's the warranty (Score:2, Informative)

    by Cheech Wizard ( 698728 ) on Wednesday December 31, 2008 @06:21PM (#26285751) Homepage
    Look at the warranties for 'Whole House' backup power generators before buying. I got a Kohler 17KW natural gas/propane and automatic transfer switch with a 5 year full guarantee (Mine is natural gas, but an orifice change is all that's needed to run it on propane). And it's really quiet. It sits outside my bedroom wall and it's little more than a bit of a hum (easy to sleep through). But it was expensive to buy and install, and it's expensive to run, but when you need it, it's very appreciated. 17KW will handle most gas homes, but if you have all electric you better be looking at 25KW+. Those have small car engines in them (liquid cooled) and they REALLY suck up the gas. NOTE: Assume 150 hours to an oil change and 300 hours for plugs, so if you are expecting to be out for a week or more you'll need extra oil, oil filters and possibly a couple of extra spark plugs.
  • by JWSmythe ( 446288 ) * <jwsmythe@nospam.jwsmythe.com> on Wednesday December 31, 2008 @06:31PM (#26285851) Homepage Journal

        It depends on what tank you put with it. :) I don't see a spec for the tank on either the Home Depot site, nor the Guardian site. It does indicate that it runs on LP or natural gas. I would guess the assumption is that you can use it with your local supply, assuming you're in an area that you can get gas.

        I have a neighbor a few miles away that has natural gas at his house. Now, I don't know if that's affected if the power to the area goes out.

        The indicated fuel consumption at full load is:

        Natural Gas - 139 cubic feet/hr
        LP - 68 cubic feet/hr (1.68 gal/hr)

        A 20 pound tank, like you'd use for your BBQ, is approximately 4.1 gallons, or about 2.4 hours.
        A 250 gallon tank would last you for about 6 days.
        A 500 gallon tank would last you for about 12 days.

        According to These reports [dslreports.com] you'll be paying about $3 to $4 per gallon. This will vary by your location, current market value, etc, etc. If you were to need to run a week on propane, because of ... well, whatever ... It will consume approximately 280 gallons of fuel, and cost you pretty close to $1,000.

        Now, if you fill the tank once, and only need a few hours here and there, then it's not a big deal. Just have it topped off every so often. How important is your power to you though? Can you get away without a computer, and camping around the fireplace? It's probably cheaper. :) The kids will make noise without the TV and PS3/Xbox360/GameThing(tm). Can you survive? Maybe they'll have to communicate. If they get too noisy, throw them out in the snow. They'll shut up just to be able to stay inside. :)

  • by llefler ( 184847 ) on Wednesday December 31, 2008 @06:54PM (#26286087)

    You're comparing apples and oranges here. In your example you have a low rated wire with a higher rated circuit interrupt. A load that exceeds the capability of the wire will cause it to melt rather than tripping the breaker.

    The generator in the parent is a power source, not a power draw, and the circuit interrupt is rated lower. If the power draw from the house is higher than 15 amps, the the circuit will trip disconnecting the draw from the source. Any reasonable generator will throttle back based on load. I don't see how this is different than your primary source, the transmission lines, being capable of considerably higher current than your house mains.

    While I personally would want the wiring and transfer switch rated higher than the generator, I doubt it's the invitation to calamity that you imply.

  • by JWSmythe ( 446288 ) * <jwsmythe@nospam.jwsmythe.com> on Wednesday December 31, 2008 @07:45PM (#26286525) Homepage Journal

        Burn the furniture. When that runs out, burn the neighbor's furniture. As far as that goes, a good house bonfire does wonders for keeping warm, even if only for a little while. Your neighbors may not appreciate it, especially if they're home. :)

  • by Muad'Dave ( 255648 ) on Wednesday December 31, 2008 @08:25PM (#26286921) Homepage

    Well, let's see. 2500 square feet of finished space. 1250 square feet of unfinished basement. Two heat pumps, one 2.5 ton, one 2 ton. A large (but EnergyStar) fridge. A '3 Jimmy Hoffa' freezer, 220V big amperage well pump. Macerating sewage ejector pump. All your normal AV and networking gear, powered by a 2400W inverter and bank of 6 110Ah gel cells to hold power until the gen comes online. The inverter has a 120V 30A charger _in addition_ to the 20A of load it can power. With the exception of the clothes dryer and stove, the usual high current suspects are propane-powered - instant-on Rinnai water heater, backup heat, 2 gas fireplaces, cooktop, etc.

    If you do the worst-case startup current, assuming that both heat pump compressors try to start when the generator takes the load, then 20 kW is reasonable.

    The 200A transfer switch is required by code because it is my 'service panel'. What you would call the main breaker panel is technically just a subfed panel. In fact, there's no main breaker in my breaker box!

    That all said, the point of the generator is not to weather outages when we're home, but to run the house, no matter the state it's left in, when we're not there. I've come home from the Caribbean to 4 feet of water in my basement for the last time. (This basement is poured concrete, and is a walkout design. The one that flooded was a conventional block basement).

    This search [google.com] gives a few resources to calculate the required capacity for generators. This one [google.com] is from my local utility, and this one [guardiangenerators.com] is from Generac. Entering my data returns a 15-20kW unit.

  • by Dun Malg ( 230075 ) on Thursday January 01, 2009 @12:00AM (#26288485) Homepage

    I have a neighbor a few miles away that has natural gas at his house. Now, I don't know if that's affected if the power to the area goes out.

    Natural gas runs without electricity. Gas utility service runs at negligible pressure (3 psi nominal, down to 0.5 psi functional), so the available pressurized storage (gasholders, underground, or line packing) is unlikely to run out in the absence of electricity.

  • by mysidia ( 191772 ) on Thursday January 01, 2009 @12:12AM (#26288545)

    Thankfully, I don't have any "main" breaker whatsoever, so there's no risk, yep.

    An approved transfer switch or interlock is the ONLY legal way to connect a generator, if you also have utility power service.

    If you ever think you have to turn off the main breaker to prevent a backfeed, you are making an illegal connection.

    Also, there is no guarantee that a breaker prevents a flow of current from OUTPUT terminal to INPUT terminal. Most breakers can without damage to the breaker, in practice.

    But plug-in breakers are popular, these are not sufficiently secured.

  • Re:tips (Score:3, Informative)

    by unitron ( 5733 ) on Thursday January 01, 2009 @02:43AM (#26289149) Homepage Journal

    Prices are coming down right now, and the difference between direct burial and using PVC conduit may be close enough that I'll just go with direct burial. Of course, throwing in some conduit doesn't hurt either, if you're ever thinking of adding something like CAT5 for Internet or phone.

    Never run low voltage wiring (telephone, TV cable, intercom, thermostat, ethernet, et cetera) in the same conduit with "electrical" wiring (120 and/or 240). It's a violation of the National Electrical Code, which in most jurisdictions has the force of law, and it's unsafe in a number of ways.

    Also, the NEC has specific requirements concerning how large an inside diameter the conduit has to have, depending on how many of what gauge wires are run through it.

    If you're going to run both low voltage and power conduits in the same ditch, make it wide enough and deep enough to allow for some vertical and horizontal separation between them, and mark which are which every foot or so for the sake of safety and convenience.

  • by afidel ( 530433 ) on Thursday January 01, 2009 @03:23AM (#26289281)
    Because there are VERY few places where you can get a big enough natural gas service hookup to power a .5MW generator! As far as using a big storage tank? That's just a non-starter for most commercial applications, zoning just won't allow it. Diesel's hard to burn and basically can't explode outside an engine, that's quite a different beast than compressed natural gas (search youtube for bleve to see what I mean)
  • by ormondotvos ( 936952 ) <ormond@lmi.net> on Thursday January 01, 2009 @06:43PM (#26294055)
    I usually cruise /. for useful information, but this subject I know frontwards and backwards and there's a LOT OF BAD ADVICE BEING GIVEN. Talking about 200 amp transfer switches is a dead giveaway that you're talking to someone who has seen it done once somewhere, but has not theory. Talking about building a shed outdoors means they're not familiar with cooling requirements. The Honda eu3000i has a remote start option. It's about 80$ for a reasonable size transfer switch, with instructions, from Home Depot or similar. You can have a male plug dangling from one side of the transfer switch. By definition, it will not be hot, ever, unless it's plugged into the generator. The purpose of the transfer switch is to isolate the power lines from the generator, and to allow the house to look like a single appliance. It is a felony that will be prosecuted to connect your generator to the power lines, not to mention that: if the power comes on, the surge between your out of phase generator and the powerlines will likely hurt your generator, which is trivial compared to getting arrested for manslaughter for killing a power line worker. There is a natural gas carburetor kit available for the eu3000i, so if you have natural gas, you have house heat and electricity, perhaps three times as cheap as gasoline. I've worked out the figures, and at the current natgas costs, the generator is almost as cheap as grid electrics. You can do it yourself, using $/Btu for gasoline and natgas as the apples to apples comparison. The Honda is extremely quiet and cleanrunning and cools the muffler with the motor/generator airflow. It does produce carbon monoxide, so be sure to completely isolate the generator exhaust airflow from any possible air input to the house, like doors, windows, or leakage from the basement. Put it outside, use a big chain through the handle. It only weighs 70#. It's really a gas engine with a huge alternator built into the flywheel, that puts out rectified AC to an ultracapacitor that's tapped by a 3Kw inverter as needed. The charge level of the capacitor determines engine speed, so it doesn't waste gas running fast when load is low.